Please share the monitoring you mentioned
...
OK - you asked for it!
Commercial datalogging kit can get very expensive and historical smart meter data is not always easy to get hold of and, at half hour resolution, is not particularly helpful when it comes to disaggregating loads. There are some homebrew options such as those at
https://openenergymonitor.org/ which use Aruino/Raspberry Pi as a basis to build a logging system from the bottom up.
In practical terms a standalone logger is often the easiest way to grab some data for diagnostics. These millivolt loggers are getting hard to find now but are a (relatively) low cost solution for getting high resolution data:
https://cpc.farnell.com/lascar/el-usb-act/data-logger-w-current-clamp-input/dp/IN07964The logger plugs into a split core current transformer with a millivolt output (something like this
https://uk.rs-online.com/web/p/current-transformers/9145294) which clips round the line or neutral on your consumer unit. This is non-invasive and does not involve cutting into live wires but obviously if there is
any doubt you should consult an electrician.
This logger will record 127,000 time stamped data points, so at a resolution of one reading per minute (say) it will log for up to 88 days, although you can stop/download/restart when ever you want. The two AA batteries will last about four months at this resolution. The logger connects to the PC via USB to set parameters and to download the data when you are done. The logger software is free and reasonably simple to use on a Windows PC.
The output is current in amps which is all you need to see the consumption patterns but you can convert to power by multiplying by the fixed voltage at your home (~230 V). If you multiply the power in kW by the duration of the logger time step in hours (1/60 at a one minute resolution) you get energy in kWh (on your bill one 'unit'= 1 kWh). Note that strictly speaking this will give you 'apparent power' (in kVA) so might not agree completely with your meter which measures 'real power'. This is not the place to go into AC power theory but there is a beer analogy here which explains it loosely:
https://www.fluke.com/en-us/learn/blog/power-quality/power-factor-formulaIf you plot the current/energy data in a spreadsheet as a simple line chart the consumption pattern will give you a good idea of what is using the power. Fridges and freezers for example have a distinct on/off cycle which usually shows itself overnight. You can make a note of when you run dishwashers, washing machines or other appliances and you will soon recognise their signature in the chart. As well as the peak loads (when things switch on) it can be very useful to see what your baseload is - this is the stuff that is on all the time and will show as a consistent low load across the monitoring period. Because the baseload it there 24/7 it can comprise a large portion of your electricity consumption.
If this sounds complicated it is because it is, but once you have your head round it the results are often fascinating.